RCD keeps tripping

My RCD keeps tripping and I can't find anything obvious that's doing it. Most of the appliances have been unplugged and I still can't figure it out. The entire system trips and not just a single fuse. Does anyone have any advice on how to find the fault?

Asked by Abdul on 31st Mar 2020
Expert Trade Answers
"Remove every single thing plugged in from the sockets and reset the RCD. Then plug things back in one by one and see if it trips."
Answered on 31st Mar 2020 - Member since Nov 2019 - report
"Switch off all circuits then reinstate the RCD. The RCD should no longer trip. Then reinstate each individual circuit one by one and when switching up the faulty circuit RCD should trip. You now know what circuit is the cause of the issue. Leave that switched off and reinstate all other circuits. Check on fuse board to see what circuit is the issue. That will then narrow down your search as well as enabling other circuits."
Answered on 31st Mar 2020 - Member since Aug 2019 - report
"Hi, this could be the faulty RCD itself. They are only by manufacturer instructions supposed to trip a set amount of times. Difficult to answer without seeing this.

What circuits are on the side that trip? Does the RCD cover all the circuits or is it a split board (2 RCDs covering two lots of circuits)

The side that trips, does this by any chance have a light circuit on it? Or any outside lights?

Lumia"
Answered on 10th Apr 2020 - Member since Nov 2019 - report
"Get an electrician to come over and have a look at it!
Needs to be inspected by a QUALIFIED Electrician instead of someone "having a go at it "!!"
Answered on 31st Mar 2020 - Member since Feb 2020 - report
"There could be a potential earth leakage to. If all appliances are unplugged then it seems like earth leakage between the cables."
Answered on 31st Mar 2020 - Member since Mar 2020 - report
"First of all put all the small mcb down and unplug everything then turn the rcd up and hopefully it holds if it does then slowly start lighting up the mcb one at a time if it trips when you put a certain one up this will tell you what circuit Is the problem."
Answered on 31st Mar 2020 - Member since Dec 2018 - report
"Call out an electrican as there are a lot of probable causes, all of which must be checked by a domestically qualified electrician."
Answered on 31st Mar 2020 - Member since Mar 2019 - report
"Sounds like an earth fault. You should hire a competent electrician to fault find the problem that is causing one of of your rcd's inside your consumer unit to trip."
Answered on 10th Apr 2020 - Member since Dec 2019 - report
"Nuisance tripping, faulty rcd. Water ingress somewhere, or mice somewhere, turn all circuit breakers off, see if rcd stays on, turn on 1 by 1 to eliminate."
Answered on 31st Mar 2020 - Member since Jan 2019 - report
"Hi. You need first to locate the circuit (fuse) where the fault appears. Turn down all fuses, put up the RCD and one after another put up each fuse. That will indicate the fault circuit. Usually, there is a wire, box or something that is wrong."
Answered on 31st Mar 2020 - Member since Mar 2020 - report
"You will have to unplug everything and turn everything off then see if still tripping if so a test for insulation resistance will need carried out at the consumer unit but you must be qualified and have the equipment to carry out this test sounds like you have a short in a cable or faulty socket, switches etc.
The easiest way to repair is get a qualified electrician to check the fault out."
Answered on 31st Mar 2020 - Member since Mar 2020 - report
"You need to hire a qualified Electrician to investigate and with a view to remedy the fault within scope; failing that give you quote to remedy the problem noted"
Answered on 5th Apr 2020 - Member since Apr 2020 - report
"Take the neutrals out for every circuit on that side of the rcd. Keep all the mcbs off. Once you have taken out each neutral, switch the rcd to on and it’ll stay up, Touch the mistral bar with each disconnected neutral cable that you had previously disconnected and eventually the problematic circuit will knock out the rcd. You then know which circuit is causing the issue."
Answered on 31st Mar 2020 - Member since Jul 2019 - report
Find Tradespeople, compare up to 3 quotes!
It's FREE and there are no obligations
Ask a Trade
Got a question that only a tradesperson can answer? We have thousands of trades ready to answer any question you may have.
Ask your question
Ask a Trade

Are you looking for advice on a DIY project or have a question for our tradespeople?

We'll email your question to tradespeople who are skilled in your chosen category.

Your question will be made public - please do not include any personal details.

{{ first(ask.errors)[0] }}

By continuing you agree to the Community Guidelines.

Report Content

{{ first(reportForm.errors) }}

Thank you

Your report has been created and will be investigated shortly.

Ready to get a price for your home improvement project?
Get started

Over 1 million homeowners and over 50,000 tradespeople
use MyJobQuote nationwide each year