CAN A 4.8KW DOUBLE OVEN FED FROM 2 X 2.5 TWIN & EARTH CABLES ON 32 AMP MCB

CAN A 4.8KW DOUBLE OVEN FED FROM 2 X 2.5 TWIN & EARTH CABLES ON 32 AMP MCB

Asked by Michael on 16th Oct 2024
Expert Trade Answers
"More information required to answer this correctly.

If the oven was the sole appliance on the ring main, then yes. However, my feeling is, you'll have other appliances on this ring main. Depending on the distance from your distribution board you would ideally/commonly have a 6mm or 10mm cable. You should get a qualified electrician to calculate what is required and have them install it for you. If it is a new circuit, it will also require certifying."
Answered on 27th Oct 2024 - Member since Oct 2024 - report
"Better off with 1 4mm if short distance or 6mm if more than 10 metres as a guide"
Answered on 16th Oct 2024 - Member since May 2020 - report
"I would say not this sounds more like a ring circuit. If you have a cooker switch then it should have a 6.0 or 10.0 mm cable which would be ok"
Answered on 16th Oct 2024 - Member since Apr 2024 - report
"2.5mm twin and earth cable for 4.8kw double Oven. The current carrying capacity of the 2.5mm twin and earth cable is dependant on the method of installation as on o.s.g variable
And it also depends on the ambient temperature
Better off use 6mm2 as it is usually used for Cooker"
Answered on 17th Oct 2024 - Member since Sep 2024 - report
"It will work but definitely not ideal as that draws 20amps at full blast so if you put the kettle on at the same time it would trip. Needs its own 32amp supply"
Answered on 22nd Oct 2024 - Member since Aug 2024 - report
"What's the actual question?

Regardless, 4.8kW is equal to about 20amp with a nominal voltage of 240v.
Current Carrying Capacity of 2.5mm Twin&Earth is 28amp or 42amp on a ring. So Ib / In / Iz requirements are met.

Therefore, yes, it should be fine. But also should befused down to a 20amp MCB or RCBO."
Answered on 16th Oct 2024 - Member since Mar 2022 - report
"Hi,

Basically a 4.8kw oven is around 20.8 amps you should not spur off kitchen ring to feed the oven as there a very good chance you will trip your electric if your are cooking and using appliances at the same time. The 2.5mm cable takes 27 amps clipped direct so that's fine but in modern regulations anything over 2kw goes on it own supply. If there is a cooker supply of some sort you could use that but you really need to consult an electrician."
Answered on 16th Oct 2024 - Member since May 2023 - report
"4800/230=20.8 amps so no problem with using 2.5mm twin and earth, for best practice however consider wiring to its own mcb (20 amps) and not from an existing ring main,"
Answered on 16th Oct 2024 - Member since Sep 2024 - report
"Simple answer to this is a no. Anything significantly above 2kW shouldn't be permanently connected to a ring final circuit.

Extended answer directly from the regs below

Appendix 15 of BS7671 (wiring regs) covers ring final circuit arrangements and states ''The load current in any part of the circuit should be unlikely to exceed for long periods the current carrying capacity of the cable. This can generally be achieved by (iii) connecting cookers, ovens and hobs with a rated power exceeding 2kW on their own dedicated radial circuit.''"
Answered on 16th Oct 2024 - Member since Aug 2024 - report
"Hi without being a teck yes it's fine to plug in to your 32A supply"
Answered on 16th Oct 2024 - Member since Jun 2020 - report
Find Tradespeople, compare up to 3 quotes!
It's FREE and there are no obligations
Ask a Trade
Got a question that only a tradesperson can answer? We have thousands of trades ready to answer any question you may have.
Ask your question
Ask a Trade

Are you looking for advice on a DIY project or have a question for our tradespeople?

We'll email your question to tradespeople who are skilled in your chosen category.

Your question will be made public - please do not include any personal details.

{{ first(ask.errors)[0] }}

By continuing you agree to the Community Guidelines.

Report Content

{{ first(reportForm.errors) }}

Thank you

Your report has been created and will be investigated shortly.

Ready to get a price for your home improvement project?
Get started

Over 1 million homeowners and over 50,000 tradespeople
use MyJobQuote nationwide each year